We are turning our roof into an unvented roof assembly by raising the roof and blowing in SPF. We are planning to leave the existing vapor barrier down but remove the fiberglass batting and then adding 6" of SPF in all the cavities, to completely seal and insulate the house. Should we have any concerns about doing it "upside down" and not spraying the foam directly to the underside/sheathing of the roof? http://www.youtube.com/watch?v=ggLAUsiuI_o&feature=youtu.be
The problem was that the installer was doing his first spray foam job ever, and the thickness of the insulation varied from zero (visible roof deck) to about 9". Unfortunately, good average thickness doesn't cut it. The coverage needs to be uniform because a lot of heat will go through the under-insulated areas. (See my article on flat or lumpy insulation performance.)
There are several types of reflective roof coatings that impart varied reflectance rates/ values. Typically, the reflective coatings are what are commonly referred to as white coatings and there are also aluminum coatings typically used with asphalt. Highly reflective white roof coatings are typically comprised of acrylics, urethanes, silicones, SBS, SEBS, and other types.
I did a LOT of prep before using this product. Cleaned, vacuumed, installed additional insulation etc etc etc. This spray foam was easy to work with, and did it's job as it was supposed to. If you are curious, this kit was purchased because - every "foam insulation company" I contacted either did not call back (due to no interest) OR this was too small of a job. That is why I went DIY on this one, that and: I was advised by one of these companies that they have a minimum $2k job because ... (insert your answer here, but I will choose that everyone needs to eat).

The drawback to spray foam insulation is it's been known to cause certain health issues such irritation of the eye and the gastrointestinal and respiratory tracts. Direct contact can cause inflammation to the skin, and some individuals have been known to break out in a rash on the arms, chest and neck area. Spray foam insulation has also been linked to a few cases of hypersensitivity pneumonitis. This condition can cause:
If you’re not familiar, spray foam is a type of insulation that expands after you spray. The foam expands and seals, avoiding any type of unnecessary moisture (which can create mold) or encouraging pests to eat through your walls. It protects the lining of your house, and even can protect the heating and cooling of your house during those unbearably cold or hot days.
I am on my third project with foam it green. I like the simplicity of it, the color blending to make it green, it alerts you quickly if something is wrong with the blending so you don't waste alot of valuable material. Follow the instructions closely, put in the prep time and you will have no issues. It seems most people's negative comments have to do with not following instructions or guidelines. It is about as close to point and shoot as you can get but there are still some essential details that need attention. The only complaint I have is the fragility of the gun, last project I cracked one on accident but luckily needed two kits to finish the project so I had a back up, but I was more careful to gently lay the gun down between applications. http://m.youtube.com/e/ggLAUsiuI_o
If you cut the nails holding one of the corner studs to the bottom plate and the top plate with a Sawzall, you can use a flat bar (or a flat bar plus a wrecking bar) to pull the stud off the sheathing nails. Either re-use the stud, or buy a new stud, and install the stud with toenails as shown in the link I provided in Comment #51 (this link: Outside corner detail).
Sta-Kool 780 Siliconized Acrylic White Elastomeric Roof Coating Sta-Kool 780 Siliconized Acrylic White Elastomeric Roof Coating is a high quality flexible white acrylic roof coating. Product is enhanced with silicone for improved water resistance adhesion and life expectancy. Product resists cracking peeling while offering tremendous durability and long term life. The coating forms a durable protective barrier which ...  More + Product Details Close
SPF insulation applied by professionals is usually described as either a high- or low-pressure foam and is available as either open- or closed-cell. Each type has advantages and disadvantages depending on the application requirements. The comparison chart below can be helpful in explaining or understanding which type of SPF insulation is best suited to a specific application.
Ames® Roof Coatings are premium elastomeric coatings that seal out moisture, renew old surfaces and even save energy. We have products specifically formulated for all types of roofs including; Wood, Tar, Metal, Rolled Roofing, EPDM Rubber, Foam and many other surfaces. Ames’ coatings form a waterproof seal to preserve and protect your roof. Our white roof coatings reflect sunlight, substantially reducing roof temperatures. Ames® products are environmentally friendly, waterbase, non-toxic, VOC-free and water cleanup.
These coatings contain various types of acrylic polymer, and are typically formulated to help extend the coating’s life and improve durability. Acrylic coatings are available in a number of colors but are most commonly used as white reflective coatings. Thanks to its durability and low cost, many contractors and facility managers believe this to be the best roof coating. http://kvsprayfoam.com/images/KV-Spray-Foam-Denver.jpg

Spray foam insulation or spray polyurethane foam (SPF) is an alternative to traditional building insulation such as fiberglass. A two-component mixture composed of isocyanate and polyol resin comes together at the tip of a gun, and forms an expanding foam that is sprayed onto roof tiles, concrete slabs, into wall cavities, or through holes drilled in into a cavity of a finished wall. http://m.youtube.com/watch?v=ggLAUsiuI_o
Acrylic coatings are typically applied in two coats, with the second running perpendicular to the first. 1 gallon per 100 square feet is a good estimate for these coatings, as they do not need to be applied nearly as thick as many other coatings. These coatings can be sprayed or roll-applied. Acrylic coatings generally require a re-coat within 2-3 years of application. https://www.youtube.com/watch?v=ggLAUsiuI_o&feature=kp
You probably have some familiarity with spray foam insulation, and you may have even used the foam that comes in pressured spray cans at home improvement retailers. This foam is know as one-part foam, meaning that it is one continuous mixture that is simply applied to the area in need. One-part foam is frequently used for sealing small gaps and cracks. http://youtube.com/e/ggLAUsiuI_o?app=desktop
When it comes to insulating the house, fiberglass tends to be the common form of insulation. However, after comparing fiberglass and spray foam insulation, it’s shocking how fiberglass tends to be the lesser of the two. Although it has deemed reliable over the years, there are way more benefits to insulating your home with spray foam. One of those benefits includes regulating the temperature of your house. http://m.youtube.com/watch?feature=player_embedded&v=ggLAUsiuI_o

During colder months, 2 component foam is very sensitive to temperature variances. Per product instructions, both tank temperatures need to be above 70°F (21°C) for at least 24 hours prior to use. All application surfaces should be clean/dry and above 60°F (16°C) prior to application. Variance outside of the recommended temperature can affect foam yield and performance.
Installing spray foam is easy to do and can dramatically improve a building or home’s energy efficiency and thermal resistance. Our closed cell foam is so efficient just 3 inches of foam appled inside of wall cavities provides an insulation value of over R18!. Our products are specially formulated for both new construction and existing homes and buildings.

Spray Foam Near Me


Water-based acrylic coatings have more than 30 years of proven performance over a wide range of substrates. It is the coating of choice for metal roofs since it is highly reflective, can be easily tinted and is not extremely slippery when damp. When used with our rust primer, even rusted roofs can be saved. TIP: If you have a metal roof or a low slope roof that doesn't pond water, consider acrylic coatings. https://www.youtube.com/v/ggLAUsiuI_o&feature=youtu.be
Spray foam insulation is typically priced by volume, meaning your cost will depend on how much material you need to use to insulate your space, although other factors may influence price as well. In most cases, the cost of spray foam insulation is more than worth it, as it's a once and done upgrade that will not only provide energy savings in your home, but also improve your home's overall comfort. http://www.youtube.com/watch?v=ggLAUsiuI_o&app=desktop
Installing spray foam is easy to do and can dramatically improve a building or home’s energy efficiency and thermal resistance. Our closed cell foam is so efficient just 3 inches of foam appled inside of wall cavities provides an insulation value of over R18!. Our products are specially formulated for both new construction and existing homes and buildings.

Spray Foam Near Me


This high R-value of 4.45 at 1 inch, polyurethane insulation expands to seal cracks, gaps, and voids in attics, walls, crawl spaces, and ceilings. Agribalance is a three-quarter pound density foam that reduces air leakage by improving energy efficiency, and reducing moisture intrusion and outside contaminants such as dust, dirt, and allergens. As a result, builders can generally install smaller, more energy-efficient HVAC systems and achieve similar, or superior comfort compared to traditionally insulated structures which require a larger, less efficient HVAC system – resulting in higher energy costs.

How Much Is Spray Foam Insulation Installed


Current guidelines recommend up to 10 inches of insulation in your attic . This is usually added to the ground, rather than the roof line, which results in the loss of your storage area, due to not being able to refit floor boards after installation. By implementing spray foam insulation to the roof line, you regain the lost 10 inches, thus increasing storage, height and practicality.


Water-based acrylic coatings have more than 30 years of proven performance over a wide range of substrates. It is the coating of choice for metal roofs since it is highly reflective, can be easily tinted and is not extremely slippery when damp. When used with our rust primer, even rusted roofs can be saved. TIP: If you have a metal roof or a low slope roof that doesn't pond water, consider acrylic coatings. https://www.youtube.com/v/ggLAUsiuI_o&feature=youtu.be
Q. "I talked to a building product supplier for WALLTITE spray foam, he is suggesting to use 2" or 3" of closed cell-spray foam in the joists areas instead of the batts insulation. He says it will work with outboard rigid insulation. There is a location of a cantilevered floor area with steel beam so I may need to use spray foam to protect the steel beam. It would then be convenient continue to spray in the floor joist cavities and then apply 5" of polyiso outboard of the bottom cantilever floor sheathing." https://youtube.com/embed/ggLAUsiuI_o

I don't even want to ask this question but... several years ago we hired a local contractor to spray high density foam on the roof deck and walls of our unfinished 2nd floor. We realized that the job was done poorly and cut an access into the attic space to assess things. We realize now that they spray foamed directly to the chimney (no flashing). The chimney is currently used for a woodstove and DHW venting. The DHW will go away but wood stove will remain. My question is, how bad (unsafe) is this? I have found information on foam exposure to fire but have not been able to find anything about temperature ratings in general (i.e. what happens on prolonged exposure to high temperatures).

Today’s “third generation” of blowing agents have a GWP of 700 to 1000 which is still remarkably high considering water/CO2 has a GWP of 1. However, innovation from some chemical manufacturers like the Chemours Company have introduced the next generation of HFO blowing agents such as Opteon 1100, which significantly reduces the GWP impact when using closed-cell spray foam insulation products.

How Much To Charge For Spray Foam Insulation


Spray foam is a fully adhered insulation that is spray applied into wall cavities, providing a continuous air and moisture barrier. Spray foam allows efficient use of your HVAC system and helps regulate the temperature fluctuations and humidity in your home. Spray foam effectively seals the building envelope, filling in any cracks and crevices, the common source of air and moisture infiltration as well as temperature variations. http://m.www.youtube.com/embed/ggLAUsiuI_o
Wallis knows proper application of urethane products is paramount in have an effective insulation barrier. Insulation performance is also based on the R Value provided. Our minimum application is always more than adequate to give a proper R value. Wallis will never skimp on applying product. We make sure you receive what we promise as a minimum. Wallis always does a proper application of material with out worry of insulation thickness or performance. We always make sure that you are receiving the Thermal Break from heat and cold that is expected and appropriate for your needs.

once the foam is installed correctly, it is a inert plastic not much different than the foam cushions you sit on. there is not a health rick unless you have off ratio uncured foam that has not mixed properly. the foam is absolutely a health risk in its raw forms before it is mixed and cured. You should not be in the building without proper respirators and eye protection. The spray foam industry should be controlled and regulated by the same standards, testing and inspections that framing ,electrical and plumbing are. until that happens then you will have idiots with spray rigs ruining peoples homes and ruining the market for honest foam contractors that know how to price a job fairly and complete it correctly.

Where Can You Find Spray Foam


Yes, you're right that all of the problems mentioned above are related to the installer. I didn't try to hide that and even used the word 'installer' in two of the four headings. I can see how you'd think that the title is misleading, but in the end you can't separate spray foam insulation from its installation. Some people have the mistaken impression that if you get spray foam in your house, your home will outperform all others. My point here is that that's not true. https://www.youtube.com/watch?v=ggLAUsiuI_o&hc_location=ufi

Note: The practice of foam insulating the attic has raised eyebrows in the building industry because "standard" roofing techniques call for the attic to be ventilated; however, in a vented attic situation it will become approximately 130 degrees in the summer. There's no reason for an air-conditioning and vent-ductwork to have to work in that type of severe conditions. By applying Icynene right on the underside of the roof deck, the severe temperatures no longer exist in the attic. In short, the attic is now a "conditioned" space of the house that is just as comfortable as any other room in the home. This is called a "Compact Roof", which means you can frame right up against it. The one drawback of using expanded foam on the inside of the roof is that this will cause the temperature of the shingles to rise, but how much is not yet known. And how much damage a rise in temperatures could cause is debatable.
As mentioned above elastomeric coatings can be used to fix almost all types of roofs. Examples of common roof types that will work well with elastomeric coatings include; wood, polyurethane foam, single-ply roofing, modified bitumen, metal roofs, concrete and built-up roofing. If you aren't sure your roof type will work well elastomeric coatings, do not hesitate to contact us. Our experts are always willing to help.
If your foam pulled away just a little bit, Jamie, and they were able to fix it with just a little bit of touching up, then it wasn't as bad as the house where I saw this problem. As the last photo above shows, it had pulled away significantly from the studs and rafters, and it was all over the house. This was closed cell foam, and interestingly, it didn't pull away from the horizontal framing members, just the vertical and sloped ones. They did some touch up, but that wasn't enough. I don't know how this one ended up getting resolved. I think maybe the contractor came back and sprayed cellulose on top of the foam.

RE: my June 12 post...We went ahead and had the attic sprayed with a Soy-based product. Stayed in a hotel for 3 nites. Still smelled a little bad but that's gone away over time. I'm very glad we didn't use the other foam as even that much outgassing of a petrochemical could have sent my wife to the hospital. Unfortunately, the spray crew didn't speak English(at least not to me) and were kinda lazy, so they ended up spraying over some can fixtures from the kitchen below that were not insulation-contact rated. So I hired an electrician to come out, pull down the cans, pull out what he thought was an appropriate amount of foam to create a big enough air space and then re-install the cans. I billed the firm for the electrician plus an extra night we had to stay in the hotel and they paid, no questions asked. Guess they knew they had screwed up.  

How Much To Spray Foam A Pole Barn


Loctite TITE FOAM Window and Door is a Loctite TITE FOAM Window and Door is a new generation of polyurethane-based insulating foam sealant that expands to fill seal and insulate around window and door jambs. Loctite TITE FOAM is a minimal-expanding foam based on purified and concentrated ingredients that provides four times more density versus conventional window and ...  More + Product Details Close

How Much Is Spray Foam Insulation Installation


DID YOU KNOW? Spray FOam insulation out-performs conventional insulation materials because they (conventional insulation materials) trap still-dry air and if that air moves or becomes wet, the thermal resistance can drop by 50%. Spray Foam protects against air infiltration, which can increase energy costs in buildings by 10 to 40%. Eliminate these drafts and live in a more energy-efficient, comfortable and healthier building by choosing spray foam insulation.

How Much For Spray Foam Insulation In Attic


Whether you’re sending something fragile in the mail or keeping valuables safe during a move, secure packing is everything. To protect a delicate item, simply fill a spare shopping bag half-full with spray insulation foam and place in the bottom of a box, pressing the item gently into the bag as it hardens to cushion the item. Repeat for the top and you have a DIY custom packaging solution that can handle the rigors of delivery.

Spray foam is a fully adhered insulation that is spray applied into wall cavities, providing a continuous air and moisture barrier. Spray foam allows efficient use of your HVAC system and helps regulate the temperature fluctuations and humidity in your home. Spray foam effectively seals the building envelope, filling in any cracks and crevices, the common source of air and moisture infiltration as well as temperature variations. http://m.www.youtube.com/embed/ggLAUsiuI_o
Yes, a new roof should be coated if the building owner wants to add a highly reflective roof coating to reduce energy costs. The buyer should be aware of any warranties provided for a new roof that may violate that warranty during the period it is in force via the use of a roof coating. This will extend the roof’s service life. A reflective roof coating will reduce the heat load on the roofing assembly. http://y2u.be/ggLAUsiuI_o
I used this for the rim-joist in our home. A couple things: I put 1in solid core foam (cut to size) in each bay before using the spray foam. I also was able to do a relatively 'thick' spray to close off any potential gaps that may have existed. I turned off the HVAC and turned on some fans in the windows to exhaust out the fumes, and wore a mask (3m respirator).
Open-cell is also known as half-pound foam. It has an R-Value of 3.5-3.6 per inch, and its density is bout 0.5 pounds per cubic food. Low-density foams like these are made partially from raw biological materials Carbon dioxide or water is also used in the makeup. Open-cell uses far less material than closed-cell, but its R-Value is lower. Also, open cell requires a vapor retarder (like gypsum wallboard) and is riskier when used for roof sheathing. It's not highly recommended that you use open-cell insulation if you live in a cold climate unless you have that extra barrier. You should also compare how much money you spend versus how effective the open-cell insulation is wherever it's installed. http://www.youtube.com/watch?feature=youtube.be&v=ggLAUsiuI_o
There are two main types of spray foam to consider: open-cell and closed-cell. Open-cell spray foam has a lower R-value per inch and because of this, typically a lower price tag. The soft, low-density material is used for interior applications. Its high permeability allows for moisture to pass through, which contributes to bi-directional drying of the assembly, but it may not be ideal for all applications or climates.  http://kvsprayfoam.com/images/kv-spray-foam-insullation.jpg
United Coatings™ Roof Coat Elastomeric Coating is an effective coating for providing long-term reflectivity over a wide range of roofing substrates. The high reflectivity of Roof Coat Elastomeric Coating keeps the roof substrate cool, which not only helps prolong its longevity but also helps save on energy costs. Roof Coat Elastomeric Coating’s rich consistency uniformly covers the textured profile of various substrates, forming a flexible monolithic membrane that provides protection from normal weathering, aging, and ultraviolet exposure.
Heat which is created elsewhere that is transported by means of a fluid, such as water or in our case air. Spray foam insulation's most important attribute is the ability to air seal creating a custom airtight envelope within the building structure. The added benefit to air sealing is the ability to block convective heat transfer from interior to exterior during heating months and vice versa during cooling months, as the heat cannot escape through gaps in the buildings envelope without the aid of air movement from infiltration as a means of transport. https://www.youtube.com/v/ggLAUsiuI_o&feature=share
When it comes to insulating the house, fiberglass tends to be the common form of insulation. However, after comparing fiberglass and spray foam insulation, it’s shocking how fiberglass tends to be the lesser of the two. Although it has deemed reliable over the years, there are way more benefits to insulating your home with spray foam. One of those benefits includes regulating the temperature of your house. http://m.youtube.com/watch?feature=player_embedded&v=ggLAUsiuI_o
While the R value will vary, most ocSPF products have an R value of around 3.8 per inch. Unlike medium-density closed-cell SPF, ocSPF is not a vapour barrier. When installed at 5.5 inches or more, ocSPF does act as an air barrier. It is often used for interior walls because it provides sound reduction by blocking and absorbing air leakage. It is usually only recommended for indoor applications.

How Much To Spray Foam A Shipping Container

×